    I get the Error shown below in the Modbus Publisher Slave

    0_1475852418886_modbus-slave.PNG

    It seems like the Publisher anyway publishes, but I wonder what's the reason.

    posted in User help read more
  • mondayVision

    Hi Phil,

    thanks for your reply. To have a feature you mentioned was great! In our project i had to generate several meta points just to be able supply modbus publisher with zeroes.

    Concerning the problem mentioned, i have new findings. Initially i did not define the modbus registers linearly corresponding their address. For example i defined

    0 lenght 4 ...
    64 length 2 ...
    4 length 4
    8 length 4
    ...
    60 lentgh 4
    ...

    Now, they are ordered strictly monotonically increasing corresponding their offset.
    Problem solved!

    Should be documented somewhere maybe?

    Alex

    posted in User help read more
  • mondayVision

    I recently bought a Publisher for Modbus IP publish-ip-unlimited licence.

    Now when trying to feed a third party TCP Modbus Master, I get in trouble.

    The master needs to read multiple registers with length 120. That fails. I tried reading multiple registers with length 16, that worked. 32 didn't.

    Sadly there is no documentation about a lenght restriction IMHO.

    For my project it is really important to be able read 120 registers at once!!! If not implemented in the module, would it be possible getting that included soon?

    Anybody who can give advice?

    Alex

    posted in User help read more
  • mondayVision

    Hi all,

    in the mango help http://help.infiniteautomation.com/support/solutions/articles/14000022524-meta-data-source there is written 'see “Script execution” below' when it comes about when a script is executed.

    Sadly there is nothing written below...

    Can anyone tell me when a metadatasource is updated?

    Alex

    posted in Scripting general Discussion read more
  • mondayVision

    Hi there,

    I am about to setup mango to retrieve BACnet data from six JCI DCCs, approximately 200 data points each.

    What will be the best approach considering data sources. Should I use one data source for all controllers or better use one data source for each controller?

    Especially regarding CPU performance and best Threading behaviour.

    Best regards
    Alex

    posted in How-To read more